January 19th, 2005, 12:30 AM
#1
Inactive Member
I am strapping an existing ceiling and want to run wires within the 3/4" strapping spacing between the existing ceiling and the new gyproc. What do I need to do to protect the wiring? metal/plastic conduit? metal flashing over the wire?
thanks
-
January 20th, 2005, 02:35 AM
#2
Inactive Member
Rule 12-516 (1) Where the cable is run through studs, joists, or similar members, the outer surfaces of the cable shall be kept distant at least 32 mm(1 1/4 inches) from the edges of the members or the cable shall be effectively protected from mechanical injury. To answer your question, you could use #14 guage metal, or conduit for mechanical protection.
<font color="#a62a2a" size="1">[ January 19, 2005 10:41 PM: Message edited by: CRM ]</font>
-
January 20th, 2005, 09:13 AM
#3
Inactive Member
Excellent. Thanks for the info.
-
January 21st, 2005, 01:50 AM
#4
Inactive Member
The more protection the better. CEC states protection is required "through" not "within".